Question: [Mach3 USB Interface Board] After reset of E stop, I get error message "RnR Motion Card Not Found". Have you any advice?

Current Solution

If you are getting the message RNR Motion Card Not Found, the controller is shorting. Check the wiring to make sure you have all of the correct wires in the correct terminals. Check the voltages of all the terminals to make sure everything shows the correct polarity and voltages.

Additional Information:
Mine did the same thing. Try pushing the USB cable all the way into the port and slightly up. My usb port on the card is slightly oversized and breaking the connection. Ordering some USB type B connectors off of amazon, gonna try and re-solder a new port on the card before replacing the card.

Respond:

Other Possible Solutions to this Question

  • I had to wipe my computer due to virus and now can not download the USB software again. I get a "unhandled exception" error message. Any suggestions?

    An unhandled exception generally means that, in the program code, the program is not checking against every possible exception that could occur. Most likely, this exception is caused by some limit that is being exceeded (or the other way around). I would remove any files that could be associated with the program, like setting files, or even register configurations associated with that software. Also, make sure that you completely update your version of windows.

    Check to make sure all of the drivers are current for your graphics hardware. Make sure that your graphics hardware works in other programs as well.

    If you upgraded the Windows version, check to make sure your graphics hardware is compatible with the new version of Windows. Unhandled exception issue may be associated with graphics hardware and compatibility.

    Customer Response:
    I've given up on the wiped laptop and loaded the program on a different computer using windows 8. At first it won't operate my CNC until I read on Planet-CNC forum about loading the drivers on windows 8. All working now. Will run through the calibrations again today. Thanks

    Click the link to add information to this solution:
    I had to wipe my computer due to virus and now can not download the USB software again. I get a "unhandled exception" error message. Any suggestions?

  • [575] Do I have to use the motion driver and configuration file to use this card? The x,y,a shows that it's moving on display, but the motors aren't moving.

    Yes, the RNRMotion.dll file must be used and put in the plugins folder under the Mach3 folder.

    The XML file that I link on the Mach3 USB controller page is the file you should start with. This file will have the necessary configuration that links the Mach3 USB controller to the Mach3 control software. You can then make whatever changes you need to this configuration to tailor it to your machine.

    Do you see a quick flashing red led on the board when you press the arrow keys?

    Additional Information:

    Click the link to add information to this solution:
    [575] Do I have to use the motion driver and configuration file to use this card? The x,y,a shows that it's moving on display, but the motors aren't moving.

  • I need wiring diagram for motor to driver to usb motion card. I cannot find diagram. I have been unable to get information for a week.
  • mach3 freezes in the middle of a run, I don't get any message. I have press reset and then the jog buttons work. I have to reset the zero and start from the last line when the machine stopped. It happens mostly during the finishing part of the g-code file

    What interface board are you using? Typically, this will be an issue with the computer that MAch3 is installed. The only other component that may affect this would be the interface between the computer and the machine.

    Click the link to add information to this solution:
    mach3 freezes in the middle of a run, I don't get any message. I have press reset and then the jog buttons work. I have to reset the zero and start from the last line when the machine stopped. It happens mostly during the finishing part of the g-code file

  • The relay doesn't have a A+ B - it has signal in god. 5v. / 0 S P. This has to go to my USB motion card wiring shows v+ goes to top of coil no number and comes out the bottom to #2 the relay I got from you is not that simple

    The relay is only used for devices like routers, spindles, coolant, mist, etc. The relay works like an automatic switch and will allow current to pass when the relay is engaged.

    Click the link to add information to this solution:
    The relay doesn't have a A+ B - it has signal in god. 5v. / 0 S P. This has to go to my USB motion card wiring shows v+ goes to top of coil no number and comes out the bottom to #2 the relay I got from you is not that simple

  • [575] Hi, I have an old version of MACH3 V1.84 - Can someone tell me where to place the USB motion drive as there is no plugin folder in this version.

    Are you able to install a newer version of Mach3? If you are worried that your configuration will be lost, you can save the configuration by copying all of the XML files from the Mach folder. The XML files contain all of the settings that you applied in Mach3. Just in case the XML files are not compatible with the new version, make sure not to erase the current Mach3 that you have on the machine.

    Click the link to add information to this solution:
    [575] Hi, I have an old version of MACH3 V1.84 - Can someone tell me where to place the USB motion drive as there is no plugin folder in this version.

  • [575] I have one of these but pc says device is faulty. If i buy one from you will you be able to fix such problems

    If your PC is unable to communicate successfully with the Mach3 USB controller that you purchased, the problem can exist outside of the controller. If the problem is with the controller, then my controller will work. If the problem is not with the controller, then the problem will persist.

    Click the link to add information to this solution:
    [575] I have one of these but pc says device is faulty. If i buy one from you will you be able to fix such problems

  • I HAVE NOT SEEN ANY REFERENCES TO ENCODER FEED-BACK CAPABILITY IN OF THE HARDWARE YOU SELL. THIS A SUPPORTED FEATURE WITH HARDWARE/SOFTWARE SELL?

    I haven't delved into using encoders with stepping motors too much. From my research, you need to have a controller that can provide the closed loop control, rather than software handling that process. I have also found from my research that using encoders on stepping motors is generally used to stop the machine in the case that the motor failed to achieve the commanded position for some reason and gives the user the chance to correct and continue with the job.

    If you want proper closed loop control, it may be best to go with servos and servo controller that provide the closed loop control within the real of those two components.

    Click the link to add information to this solution:
    I HAVE NOT SEEN ANY REFERENCES TO ENCODER FEED-BACK CAPABILITY IN OF THE HARDWARE YOU SELL. THIS A SUPPORTED FEATURE WITH HARDWARE/SOFTWARE SELL?

  • [575] I cant get a 5v signal on any of the Outputs on the board. what Port# and Pin #s should I be using on Mach3?

    The Mach3 USB controller does not provide 5V output signals. The Inputs, Outputs, and PWM Spindle Speed terminals are separated from the 5V side of the board. The output terminals use the 24V portion of the controller and you will need a 24V power supply to make these outputs work.

    Please watch the video below to completely understand how the outputs of this controller work. Make sure that you are using the RNRmotion.dll plugin and that the port for each of the outputs is set to port 3.

    Click the link to add information to this solution:
    [575] I cant get a 5v signal on any of the Outputs on the board. what Port# and Pin #s should I be using on Mach3?

  • why do I get the message "RnRMotion.dill was blocked because this type of file can harm your device"?

    Rnrmotion.dll is a dynamic link library that is very similar in function to an executable program, or app. Since a dll is executable, malicious code can be embedded in that type of file, so windows will automatically flag all files of this type. You just need to make sure you are downloading from a trusted source. The emotion.dll file on our site is clean, but still, run windows defender against it to make sure.

    Click the link to add information to this solution:
    why do I get the message "RnRMotion.dill was blocked because this type of file can harm your device"?

  • 2017 Mach 3 usb motion card not translating commands to machine. Second green led by limit switch terminals. Seem new. MDI won't move spindle. Any Ideas?

    The mach3 USB controllers that we stock don't have green LEDs. Can you tell me what brand you are referring to?

    Click the link to add information to this solution:
    2017 Mach 3 usb motion card not translating commands to machine. Second green led by limit switch terminals. Seem new. MDI won't move spindle. Any Ideas?

  • [575] after coplete work all axis are not coming in orign point but mech3 show all axis are origen point

    To bring the machine to the origin, click the "Ref all Home" button. The machine will move to the limit switches. If the axes are not zeroed automatically, you can zero them by pressing the zero button for each axis in the digital readout (DRO) section.

    Click the link to add information to this solution:
    [575] after coplete work all axis are not coming in orign point but mech3 show all axis are origen point

  • I am getting that radus error in Mach3 and changing my IJ setting is not working. Any suggestions?

    What is the actual error that you are seeing in Mach3 and what CAM program are you using? Did you try installing a later version of Mach3 if your's is an earlier version? What post-processing setting are you using in your CAM program?

    Click the link to add information to this solution:
    I am getting that radus error in Mach3 and changing my IJ setting is not working. Any suggestions?

  • How can we check our 1.5kw spindle. we get a dL error after we start to cut. it spins up fine. We checked IGBTs in the VFD and they're not shorted. We suspect intermittent short INSIDE the spindle. What do you think?

    dL usually stand for a short that is occurring within the spindle or spindle wiring. I would recheck the wiring going from the VFD to the spindle, as well as the terminal on the spindle where there should've been some soldering required. We usually tend to either heat shrink or use electrical tape to cover the terminals so no contact or arching can be present.

    Also depending on the VFD you have please adjust the setting pd008, to the voltage that is required (110V/220V).

    If the issue proceeds please contact use at customerservice@buildyourcnc.com, for further assistance or replacement.

    Click the link to add information to this solution:
    How can we check our 1.5kw spindle. we get a dL error after we start to cut. it spins up fine. We checked IGBTs in the VFD and they're not shorted. We suspect intermittent short INSIDE the spindle. What do you think?

  • [575] I have my probe conected and have checked continuity but my probe does not show to be working. What else could be wrong?

    Try the probe connected between the input and DCM with just wires connected to those terminals. When you short the two wires, you should see the change in the diagnostic screen.

    Make sure that the probe configuration is correct:
    Config -> ports and pins -> inputs tab
    on the probe line, make sure the pin number matches the IN number on the controller. Make sure that the port number is 3. And finally, make sure the active low is set correctly. Toggle the active low to toggle the normally open and normally closed state of the probe.

    Additional Information:
    Nothing changes in the diagnostic screen, however the Digitize led is lit. One wire on in4 the other on DCM. If I were to put a multi-meter to any of the pins would there show any voltage?

    Click the link to add information to this solution:
    [575] I have my probe conected and have checked continuity but my probe does not show to be working. What else could be wrong?

  • I HAVE NOT SEEN ANY REFERENCES TO STEPPING MOTOR ENCODER FEED-BACK FOR CLOSED LOOP CAPABILITY IN OF THE HARDWARE YOU SELL. THIS A SUPPORTED FEATURE WITH HARDWARE/SOFTWARE SELL?

    I haven't delved into using encoders with stepping motors too much. From my research, you need to have a controller that can provide the closed loop control, rather than software handling that process. I have also found from my research that using encoders on stepping motors is generally used to stop the machine in the case that the motor failed to achieve the commanded position for some reason and gives the user the chance to correct and continue with the job.

    If you want proper closed loop control, it may be best to go with servos and servo controller that provide the closed loop control within the real of those two components.

    Click the link to add information to this solution:
    I HAVE NOT SEEN ANY REFERENCES TO STEPPING MOTOR ENCODER FEED-BACK FOR CLOSED LOOP CAPABILITY IN OF THE HARDWARE YOU SELL. THIS A SUPPORTED FEATURE WITH HARDWARE/SOFTWARE SELL?

  • I received a VFD 110v yl600-2s-2k20 p 110v with 220v instructions, also the connectors on the VFD dose not match any wiring configuration you have.

    Ok, I will check the YL600 documentation Monday 4/3 and provide the answer here.

    Additional Information:


    Additional Information:
    I also received one of these and the button labels do not even match your programming instructions as stated on your web set. Please provide updated instruction to match the model shipped with the correct button names to press in The programming process.

    Additional Information:
    7/15/17 - I have exact problem. I do not see the solution posted???

    Additional Information:
    Mine is a 2.2Kw YL-620 connected to a 1.5Kw spindle.

    Code Address Function Set Range &Function Explanation Factory Setting User Set Vendor Suggested As shipped Code Address Decimal
    P00.00 0 Main Frequency 0-120HZ(400HZ) 50.0HZ  400 60 399.6 P00.0 0
    P00.01 1 Start / stop command source 0: Operator board 0 0  0 P00.1 1
    1:From external end control Electric machinery,operation panel STOP key effective
    2:From external end son control Electric machinery,operation panel STOP key invalid
    3:from (Modbus Rs485) control Electric machinery
    4:By user application program control Electric machinery
    P00.02 2 Reserved   0   0 P00.2 2
    P00.03 3 Stopping Mode 0:Decelerating stop 0 0  1 P00.3 3
    1:Coasting stop 10
    2:DC brake stop 0.2
    P00.04 4 VF:Highest output frequency 1.0-120.0HZ(400HZ) 50.0HZ 400 60 400 P00.4 4
    P00.05 5 VF:Maximum Voltage Output Frequency 5.0-120.0HZ(400HZ) 50.0HZ 400 60 400 P00.5 5
    P00.06 6 VF:Highest output Voltage 10.0%-150.0% 100.00% 100.00% 100.00% 100 P00.6 6
    P00.07 7 VF:Middle Frequency 1.0-120.0HZ(400HZ) 3.0Hz 3.5Hz 3.0Hz 3.5 P00.7 7
    P00.08 8 VF:Middle Voltage 10.0%-100.0% 10% 20% 10% 10 P00.8 8
    P00.09 9 VF:Min Frequency 0-120.0HZ(400HZ) 0.2HZ 0.2Hz 0.2Hz 0.2 P00.9 9
    P00.10 10 VF:Min Voltage 0%-100.0% 5% 10.00% 5.00% 5 P00.10 10
    P00.11 11 Analog Input quantity 1 Regulation Multistage velocity 0%-100% 100 100 100 100 P00.11 11
    P00.12 12 VF :Curve Setting 0-4 0 0 P00.12 12
    P00.13 13 Parameter Lock 0: lnvalid 0 0 P00.13 13
    1: Valid
    10: Restore the factory setting No other function
    P00.14 14 Reserved 0 0 P00.14 14
    P00.15 15 Power on Time prohibit External end son Start-up 0:Power on time,allow External end input effective level,start-up Electric machinery 0 0 P00.15 15
    1:Power on time,Not allow
    P00.16 16 0: FWD(X5)yes,Positive run the 0 P00.16 16
    1: REV(X6) Determine direction : Open Yes
    2:X_EF=EF,X_REV(X5)_DIR=DIR,FWD(X6)=
    3: Stop ,FWD(X5) turn off Instantaneous
    4: FWD(X5) turn off Instantaneous
    5: FWD(X5) turn off Instantaneous
    6: Stop ,FWD(X5) turn off Instantaneous
    7: REV(X6)When open,FWD(X5)Start-up
    P00.17 17 Many function input X1 function Choice ####################################### ####################################### 1 1 P00.17 17
    P00.18 18 Many function input X2 function Choice 1.0HZ 1 P00.18 18
    P00.19 19 Many function input X3 function Choice 1 P00.19 19
    P00.20 20 Many function input X4 function Choice 1 P00.20 20
    P00.21 21 External Terminal rise/Slow down increment 0-120HZ(400HZ) 1.0HZ 1 P00.21 21
    P00.22 22 External Terminal rise/Slow down time interval 0.2 0.2 P00.22 22
    P00.23 23 Physics amount display Proportion constant 0-999.9% 100.00% 100 P00.23 23
    P00.24 24 After power supply, display project choice 0: Display current target frequency 0 0 P00.24 24
    1:Display Electric machinery run frequency.
    2:Display Electric machinery run current.
    3:Display input AC voltage
    4:Display mother Line voltage
    5:Display output voltage
    6:Display speed paragraph Number SP x
    7:Display inverter temperature t xx
    8:Display input signal X1-X3/output signal
    9:Display user variable
    10:Display user Count value
    11:Display temporary debugging variable
    12:Display automatic multi segment run step and time
    P00.25 25 Display project automatic Return delayed time (10/S) 0:No,Automatic return;1-6delayed 10-60S Back Return 1 1 P00.25 25
    P01.00 256 REV Rotation Select 0: Rev Run Enable 0 0 P01.0 256
    1: Rev Run Forbidden 0
    P01.01 257 Electric machinery Reversing wait for time 0 P01.1 257
    P01.02 258 Deceleration Prevention overvoltage setting(%) 130 130 P01.2 258
    P01.03 259 Accelerated Prevention overcurrent setting(%) 130 130 P01.3 259
    P01.04 260 Overcurrent Set up (%) 200 200 P01.4 260
    P01.05 261 Overload protection Set up (%) 130 130 P01.5 261
    P01.06 262 Overload protection time Set up (s) 120 120 P01.6 262
    P01.07 263 Undervoltage protection Set up (%) 80 80 P01.7 263
    P01.08 264 Overvoltage protection Set up (%) 150 150 P01.8 264
    P01.09 265 After shutdown, start DC Brake voltage Setup (%) 15 15 P01.9 265
    P01.10 266 After shutdown, End DC Brake voltage Setup (%) 0 0 P01.10 266
    P01.11 267 After shutdown, DC Braking Time Set up 2 2 P01.11 267
    P01.12 268 After shutdown, DC Braking Initial Frequency Set up 0.6 0.6 P01.12 268
    P01.13 269 Before start , input DC brake voltage set up (%) 20 20 P01.13 269
    P01.14 270 Before start , End DC Brake voltage Set up (%) 15 15 P01.14 270
    P01.15 271 Before start , DC Braking Time Set up 3 3 P01.15 271
    P01.16 272 Direct start Initial frequency (Improve starting torque ) 100 100 P01.16 272
    P01.17 273 Direct start Initial frequency Hold time 0 0 P01.17 273
    P01.18 274 power failure frequency decline 80 80 P01.18 274
    P01.19 275 The power down frequency decline rate 5 5 P01.19 275
    P01.20 276 Restart No load time 10 10 P01.20 276
    P01.21 277 Restart voltage rise time 200 200 P01.21 277
    P02.00 512 When speed up torque will increased   100  100 100 60 P02.0 512
    P02.01 513 Deceleration time - Torque Boost   100  100 100 60 P02.1 513
    P02.02 514 Accelerate curve Choice 0  0 P02.2 514
    P02.03 515 Deceleration curve Choice 0  0 P02.3 515
    P02.04 516 Avoid the f requency 1 20 400 P02.4 516
    P02.05 517 Avoid the f requency 2 30 30 P02.5 517
    P02.06 518 Avoid the f requency 3   40 40 P02.6 518
    P02.07 519 Avoid the f requency Width   0 0 P02.7 519
    P02.08 520 Window frequency 1 45 45 P02.8 520
    P02.09 521 Window frequency 2 50 50 P02.9 521
    P02.10 522 ? 400 P02.10 522
    P03.00 768 RS485 Communication Baud Rate 0: 1200Bps 5 4 P03.0 768
    1: 2400Bps
    2: 4800Bps
    3: 9600Bps
    4: 19200Bps
    5: 38400Bps
    6: 57600Bps
    P03.01 769 RS485 Communication Addresses 1-254 10 10 P03.1 769
    P03.02 770 0: 8 bit data, 1 stop bits, odd parity 2 2 P03.2 770
    1: 8 bit data, 1 stop bits, parity check
    2: 8 bit data, 1 stop bit, no parity
    3: 8 bit data, 2 stop bits, odd parity
    4: 8 bit data, 2 stop bits, parity check
    5: 8 bit data, 2 stop bit, no parity
    P03.03 771 Communication error handling 0 P03.3 771
    P03.04 772 Communication error tolerance time 20 P03.4 772
    P03.05 773 4-20mA Break detection time 0 P03.5 773
    P03.06 774 Panel potentiometer,Lower limit of AD norm 3 P03.6 774
    P03.07 775 Panel potentiometer,Upper limit of AD specification 1020 1015 1015 P03.7 775
    P03.08 776 Panel potentiometer, frequency given of lower limit 0.0HZ 0 0 P03.8 776
    P03.09 777 Panel potentiometer, frequency given of Upper limit 0-120HZ(400HZ) 60.0HZ 400  60Hz 400 P03.9 777
    P03.10 778 Analog lnput 1 AD lower limit 0-1023 3.0Hz  60Hz 3 P03.10 778
    P03.11 779 Analog lnput 1 AD Upper limit 0-1023 1020 1010 1010 P03.11 779
    P03.12 780 Analog lnput 1 frequency given lower limit 0.0HZ 0 P03.12 780
    P03.13 781 Analog lnput 1 frequency given Upper limit 60.0HZ 400 400 P03.13 781
    P03.14 782 Analog lnput 2 AD lower limit 3.0Hz 3 P03.14 782
    P03.15 783 Analog lnput 2 AD Upper limit 1020 1010 1010 P03.15 783
    P03.16 784 Analog lnput 2 frequency given lower limit 0.0HZ 0 P03.16 784
    P03.17 785 Analog lnput 2 frequency given Upper limit 60.0HZ 60 P03.17 785
    P03.18 786 Analog output correlation 0 0 P03.18 786


    P03.19 787 Analog output gain setting 100 100 P03.19 787
    P04.00 1024 Mo analog multiplier output frequency multiplier 10 10 P04.0 1024
    P04.01 1025 Mo1 Function Options 0 0 P04.1 1025
    P04.02 1026 Mo2 Function Options 1 1 P04.2 1026
    P04.03 1027 Multi-function Relay 1 Function selection 0:fault Yes Electric , otherwise power failure 0 2 2 2 P04.3 1027
    P04.04 1028 Multi-function Relay 2 Function selection 1:Running Yes Electric ,otherwise power failure 3 3.0Hz 3 P04.4 1028
    2: Reserved
    3: Arbitrary frequency arrival Time, have Electric,Related to P02-10 settings
    4: , The power down Time,have Electric
    5:, low voltage Time, have Electric
    6:, Overvoltage Time, have Electric
    7: Overcurrent Time, have Electric
    8: Nonzero velocity Time,have Electric
    9:, DC brake Time, have Electric
    10: Over torque Time, have Electric
    11: External interrupt fault Time, have
    12: Forward Time, have Electric
    13: Reversal Time, have Electric
    14: Move Time, have Electric
    15: Accelerate Time, have Electric
    16: Deceleration Time, have Electric
    17: Constant speed Time, have Electric
    18:X1 close Time, have Electric
    19:X2 close Time, have Electric
    20:X3 close Time, have Electric
    21:X4 close Time, have Electric
    22:X5 close Time, have Electric
    23:X6 close Time, have Electric
    24: Forward and bus voltage greater than 400V Time, have Electric
    25: Reverse and bus voltage greater than 400V Time, have Electric
    P04.05 1029 Multi-function Relay 1 Action close Delayed 0-65.5 S 0 0 P04.5 1029
    P04.06 1030 Multi-function Relay 1 disconnect delay action 0-65.5 S 0 0 P04.6 1030
    P04.07 1031 Multi-function Relay 1 Action close Delayed 0-65.5 S 0 0 P04.7 1031
    P04.08 1032 Multi-function Relay 1 disconnect delay action 0-65.5 S 0 0 P04.8 1032
    P04.09 1033 Stall rotor detection time 0-65.5 S 1 1 P04.9 1033
    P04.10 1034 Switch amount (Di) sampling time 0-1000mS 8 24 24 P04.10 1034
    P04.11 1035 Stopping Mode 0:Decelerating stop 0 0 P04.11 1035
    1:Coasting stop
    P05.00 1280 PID Output Upper limit frequency 50 50 P05.0 1280
    P05.01 1281 PID Output lower limit frequency 25 25 P05.1 1281
    P05.02 1282 PID Given Source 0 0 P05.2 1282
    P05.03 1283 PID Values Given 0.2 0.2 P05.3 1283
    P05.04 1284 PID Output characteristic(FOR /REV) 0 0 P05.4 1284
    P05.05 1285 PID Output characteristic (FOR/REV) 0 0 P05.5 1285
    P05.06 1286 PID Proportional Gain 0-100.0 50 50 P05.6 1286
    P05.07 1287 PID Integration Time Ti 0-100.0 0-100.0 50 50 P05.7 1287
    P05.08 1288 PID Derivative Time Td 0-100.0 0-100.0 50 50 P05.8 1288
    P05.09 1289 PID Deviation Limit 0-50.0 5 5 P05.9 1289
    P05.10 1290 PID Integral upper limit 50 50 P05.10 1290
    P05.11 1291 PID Given Change Time 0-600.0 1 1 P05.11 1291
    P05.12 1292 PID Feedback Filter Time 0 0 P05.12 1292
    P06.00 1536 Acceleration Time 0  0 P06.0 1536
    P06.01 1537 Accel.Time 1 0.1-6553.5 5.0 9  5.0 5 P06.1 1537
    P06.02 1538 Decel. Time 1 0.1-6553.5 5.0 8.6  5.0 5 P06.2 1538
    P06.03 1539 Accel.Time 2 0.1-6553.5 0.1-6553.5 2 2 P06.3 1539
    P06.04 1540 Decel. Time 2 0.1-6553.5 0.1-6553.5 2 2 P06.4 1540
    P06.05 1541 Accel.Time 3 0.1-6553.5 0.1-6553.5 2 2 P06.5 1541
    P06.06 1542 Decel. Time 3 0.1-6553.5 0.1-6553.5 2 2 P06.6 1542
    P06.07 1543 Accel.Time 4 0.1-6553.5 0.1-6553.5 2 2 P06.7 1543
    P06.08 1544 Decel. Time 4 0.1-6553.5 0.1-6553.5 2 2 P06.8 1544
    P06.09 1545 Accel.Time 5 0.1-6553.5 0.1-6553.5 2 2 P06.9 1545
    P06.10 1546 Decel. Time 5 0.1-6553.5 0.1-6553.5 2 2 P06.10 1546
    P06.11 1547 Accel.Time 6 0.1-6553.5 0.1-6553.5 2 2 P06.11 1547
    P06.12 1548 Decel. Time 6 0.1-6553.5 0.1-6553.5 2 2 P06.12 1548
    P06.13 1549 Accel.Time 7 0.1-6553.5 0.1-6553.5 2 2 P06.13 1549
    P06.14 1550 Decel. Time 7 0.1-6553.5 0.1-6553.5 2 2 P06.14 1550
    P06.15 1551 Accel.Time 8 0.1-6553.5 0.1-6553.5 2 2 P06.15 1551
    P06.16 1552 Decel. Time 8 0.1-6553.5 0.1-6553.5 2 2 P06.16 1552
    P06.17 1553 Jog Acceleration Time 0.1-6553.5 0.1-6553.5 2 2 P06.17 1553
    P06.18 1554 Jog Deceleration Time 0.1-6553.5 0.1-6553.5 2 2 P06.18 1554
    P07.00 1792 Frequency 1 0-120HZ(400HZ) 50HZ 50 50 P07.0 1792
    P07.01 1793 Frequency 2 50HZ 45 45 P07.1 1793
    P07.02 1794 Frequency 3 50HZ 40 40 P07.2 1794
    P07.03 1795 Frequency 4 50HZ 35 35 P07.3 1795
    P07.04 1796 Frequency 5 50HZ 30 30 P07.4 1796
    P07.05 1797 Frequency 6 50HZ 25 25 P07.5 1797
    P07.06 1798 Frequency 7 50HZ 20 20 P07.6 1798
    P07.07 1799 Frequency 8 50HZ 15 15 P07.7 1799
    P07.08 1800 Frequency source selection 1 0: Operator board (parameter: P03.06~P03.09) 0 0 P07.8 1800
    P07.09 1801 Frequency source selection 2 1: Pre-set Freq, P00.00 Set frequency value,Operation panel keyboard,Can be set directly 2 2 P07.9 1801
    P07.10 1802 Frequency source selection 3 2:No. X paragraph frequency P07.00~P07.07 2 2 P07.10 1802
    P07.11 1803 Frequency source selection 4 3: Analog Input. :P03.10~P03.13) 2 2 P07.11 1803
    P07.12 1804 Frequency source selection 5 4: external simulation amount 2 (VI2) 2 2 P07.12 1804
    P07.13 1805 Frequency source selection 6 5: (Modbus Rs485)Given frequency 2 2 P07.13 1805
    P07.14 1806 Frequency source selection 7 6: User application program, given frequency 2 2 P07.14 1806
    P07.15 1807 Frequency source selection 8 7:( Pid)Output frequency 2 2 P07.15 1807
    Other: Reserved
    Note:three control methods (P07.08) 1808 1.The motor speed is controlled by the operating panel P07.16 1808
    2.Motor speed control by external terminals (Potentiometer 10K). P00.01 set to 1, P07.08 set to 3
    3.Motor speed control by external terminals. P00.01 set to 1,P07.08 set to 1.
    P07.16 1809 Jogging Frequency FORWARD 0-120HZ(400HZ) 15.0HZ 15 P07.17 1809
    P07.17 2048 Jogging Frequency REV 0-120HZ(400HZ) 15.0HZ 13.0Hz 13 P08.0 2048
    P08.00 2049 Automatic many paragraph Running: Running direction Binary data format to set the direction of operation, see (the automatic multi segment operation, the operation of the direction set table) 0  0 P08.1 2049
    P08.01 2050 Automatic many paragraph Running: mode Choice 0:Automatic multi segment operation is invalid; 0 0 P08.2 2050
    1:After execution complete,Stop;
    2:After execution complete,Keep the last running state,Continued running;
    3:After execution complete, Repeated execution.
    P08.02 2051 Automatic many paragraph Running time Units:S/M 0:S;1:M 0 0 P08.3 2051
    P08.03 2052 Automatic many paragraph Running: No.1 paragraph Running time Automatic multi-section run time,Set up Section speed run time。Time units are determined by P08.02 Decision。Set run is 0,Indicates that this section is not executed. 10 1 1 P08.4 2052
    P08.04 2053 Automatic many paragraph Running: No.2 paragraph Running time 10 1.5 1.5 P08.5 2053
    P08.05 2054 Automatic many paragraph Running: No.3 paragraph Running time 10 1 1 P08.6 2054
    P08.06 2055 Automatic many paragraph Running: No.4 paragraph Running time 10 1.5 1.5 P08.7 2055
    P08.07 2056 Automatic many paragraph Running: No.5 paragraph Running time 10 1 1 P08.8 2056
    P08.08 2057 Automatic many paragraph Running: No.6 paragraph Running time 10 1.5 1.5 P08.9 2057
    P08.09 2058 Automatic many paragraph Running: No.7 paragraph Running time 10 1 1 P08.10 2058
    P08.10 2304 Automatic many paragraph Running: No.8 paragraph Running time 10 1.5 1.5 P09.0 2304
    P09.00 2305 frequency Range(%) 0-200% 0 0 P09.1 2305
    P09.01 2306 frequency wave Range(%) 0-400% 200 30 30 P09.2 2306
    P09.02 2307 frequency Rise time(S) 0.1-999.9 S 6.0 S 6 P09.3 2307
    P09.03 2560 frequency decline time(S) 0.1-999.9 S 5.0 S 5 P10.0 2560
    P10.00 2561 Counter reload,value 1000 1000 P10.1 2561
    P10.01 2562 Counter current value 0 0 P10.2 2562
    P10.02 2563 Timer reload,value 1000 1000 P10.3 2563
    P10.03 2816 Timer current value 0 0 P11.0 2816
    P11.00 2817 Output Status 1 1 P11.1 2817
    P11.01 2818 Output Voltage (V) 0 0 P11.2 2818
    P11.02 2819 Output Current (A) 5 5 P11.3 2819
    P11.03 2820 Output Frequency (Hz) 50 50 P11.4 2820
    P11.04 3072 Current Heatsink Temperature 25 25 P12.0 3072
    P12.00 3073 Rated Motor Current 5 5 P12.1 3073
    P12.01 3074 Rated Motor Voltage 220 220 P12.2 3074
    P12.02 3075 Motor Pole number 2-100 2 2 P12.3 3075
    P12.03 3076 Motor no-load current 10 10 P12.4 3076
    P12.04 3077 Motor no-load current detection time(S) 10 10 P12.5 3077
    P12.05 3078 Converter rated current(A) 5 5 P12.6 3078
    P12.06 3079 Converter rated Voltage(V) 220 220 P12.7 3079
    P12.07 3080 DC bus output voltage% 140 130 P12.8 3080
    P12.08 3081 Heat sink over temperature protection point 70 75 P12.9 3081
    P12.09 3082 Radiating fin temperature sensor configuration 1 1 P12.10 3082
    P12.10 3083 Abnormal reset implement wait time 120 120 P12.11 3083
    P12.11 3084 Fan Function Pattern 0:Motor running tine, start fan; 1 1 P12.12 3084
    1:When the fan operating temperature (P12.12) is exceeded,Instant start fan; When the temperature is lower than the fan temperature point,Delay about 1 minutes to close the fan;
    2:Unconditional forced start fan;
    3:Fan Inoperation;
    P12.12 3085 Cooling fan operating temperature 55 45 50 P12.13 3085
    P12.13 3086 Fan Testing 0 0 P12.14 3086
    P12.14 3087 Bypass relay closed detection 0 0 P12.15 3087
    P12.15 3088 Bypass Relay delay time 1.5 1 P12.16 3088
    P12.16 3089 Power on delay timer initial value(S) 50 50 P12.17 3089
    P12.17 3090 Electric current sensor To configure 1 1 P12.18 3090
    P12.18 3091 Automatic stable pressure function Choice 1 1 P12.19 3091
    P12.19 3092 PWM Frequency 2.0-15.0KHZ (110V13.0KHZ 220V11.0KHZ 380V6.0KHZ) 8.0KHZ 13.0KHz 13 P12.20 3092
    P12.20 3328 SVPWM Pattern 0:Three-phase asynchronous motor, 0 0 P13.0 3328
    1:Two-phase asynchronous motor (Single-phase motor, 90 degree phase difference,Starting capacitor)
    P13.00 3329 103 P13.1 3329
    P13.01 3330 600 P13.2 3330
    P13.02 3331 1 P13.3 3331
    P13.03 3332 16.24 P13.4 3332
    P13.04 3333 1 P13.5 3333
    P13.05 3584 0 P14.0 3584
    P14.00 3585 35 P14.1 3585
    P14.01 3586 0.2 P14.2 3586
    P14.02 3587 1 P14.3 3587
    P14.03 3588 0 P14.4 3588
    P14.04 3589 0 P14.5 3589
    P14.05 3590 100 P14.6 3590
    P14.06 3591 1900 P14.7 3591
    P14.07 3592 2000 P14.8 3592
    P14.08 3593 59999 P14.9 3593
    P14.09 3594 5 P14.10 3594
    P14.10 3595 20 P14.11 3595
    P14.11 3596 0 P14.12 3596
    P14.12 3597 0 P14.13 3597
    P14.13 3598 0 P14.14 3598
    P14.14 3599 0 P14.15 3599


    Additional Information:
    Sorry, that is a paste from a spread sheet, you may have to do some formatting or paste it into a spread sheet to see it better...

    Additional Information:
    I will definitely do that. Thank you so much for providing the information!!

    Additional Information:
    I also have this problem with a yl620. Is there a solution?

    Additional Information:
    Is there a wiring diagram for the 110v units. My came with a 220 volt booklet.

    Additional Information:
    my unit also came with instructions for a 220 unit. I need a 110 wiring diagram.

    Additional Information:
    These instructions are lame at best, a friend of mine ordered one of these to install on a knife grinder that I built for him, and I proceeded to setup the unit, upon connecting it to the motor, it runs the motor, but hunt's at the lower speeds, and the setting I am looking for just isn't in the list, there's some settings in the 14's that don't say what there for, can anyone help?

    Click the link to add information to this solution:
    I received a VFD 110v yl600-2s-2k20 p 110v with 220v instructions, also the connectors on the VFD dose not match any wiring configuration you have.

  • Yawl sold me a ST-USB MOTION CARD I have surched all your electronics and can't find wring instructions I need to know where to connect X,Y and Z to this controler

    To connect the stepper motor drivers to the Mach3 USB interface card, you will need to follow the wiring diagram here: https://www.buildyourcnc.com/Documents/Electric%20Wiring%20Diagram.pdf
    which can be found here: https://www.buildyourcnc.com/item/electronicsAndMotors-electronic-component-breakout-Mach3-USB-Board along with all of the other manuals associated with that interface card.

    Please note that the DC+ and DC- on that wiring diagram (power supply to thye stepper motor drivers) is not correct. The DC- is connected to GND on the drivers and the DC+ is connected to VCC on the drivers. Typically, the DC+ on the power supply is labeled V+ and the DC- is labeled either COM or V-.

    If you are having any issues with the wiring, please let me know and I will elaborate. Thanks.

    Click the link to add information to this solution:
    Yawl sold me a ST-USB MOTION CARD I have surched all your electronics and can't find wring instructions I need to know where to connect X,Y and Z to this controler

  • did you receive my order yesterday, I have not received an email and I am concerned. Norman Guerin

    Let me check

    Additional Information:
    Yes, the order is in our system for the Mach3 license and the Mach3 USB.

    Additional Information:
    I just logged in using your username and I am able to see your order details in the "[ My Account ]" link at the top of the webpage.

    Click the link to add information to this solution:
    did you receive my order yesterday, I have not received an email and I am concerned. Norman Guerin

Get Help with:
This Product
Orders
Tech Support
Sales
This Product
Order Query
Tech Support
Sales
Not logged in. Log In Register
Track Order(s)
View Order(s)
I Want to Schecule a One-On-One Paid Tech Support Session
Book an Appointment Pertaining to a BuildYourCNC Product (Free)
Ask a Quesion Below (Free):
Book an Appointment Pertaining Other Equipment ($60/half hour)
Book an Immedite Appointment Pertaining Other Equipment ($120/half hour)
Ask a Quesion Below (Free):
Waiting for response... I may not answer immediately, but I was notified on my cellular phone so my response is forthcoming. If I don't respond immediately, you can always go to the [My Account] page to see all of our chats at any time.